Thread: Over sizing the breaker question?

  1. #21

    Default

    Quote Originally Posted by performance View Post
    IF the correct plug is used, then it will be obvious, since the 6-50 is the only standard plug for single phase 220V welders and cutting equipment. The camper won't plug in.
    This may have been the case previously, but a 'standard' is not a rule, & with the emergence of multi-voltage welders/cutters this 'standard' is disappearing.
    The Miller Dynasty 200DX's we have on the job are voltage sensing from 110v to 220v & as so are equipped with a neutral (4 wires out of the machine). We wire the machine with a 30amp 4 pronged plug & then run adapters for the 220v-30amp/110v-20amp outlets we may encounter when moving from area to area.
    -at the job-
    Miller Dynasty 200DX
    Miller Syncrowave 350
    MillerMatic 250 (several)
    Millermatic 350
    Miller Bobcat 250 (Service Truck)
    Lincoln AC225 (many)
    Miller Spectrum 625 Plasma (several)
    -At Home-
    Everlast PP256
    Longevity 256PI
    "Slow is smooth, smooth is fast.."

  2. #22
    Join Date
    Mar 2011
    Location
    Apache Junction, Az
    Posts
    90

    Default

    Quote Originally Posted by kenwhite View Post
    Like I said, every branch that has a socket has its breaker sized for the cable insulation type, cable run length, # of cables bundle togther, load duty cycle, and cable AWG size to protect the wiring. It is the manufacturers responsibility to fuse/breaker if they want to protect the end user equipment from excessive damage or fire hazards.

    The breaker protects the wiring between the socket(s) and panel, it is not sized or designed to protect the equipment that is plugged into the socket.

    Oh, and my furnace is hard wired into a fused disconnect and not plugged into a 120 V wall socket - this is per the manufacturers recommendation, so be careful when you use the word every...

    Typically the minumum fuse/breaker size is recommended for proper operation so the circuit is not being interrupted often when trying to use the device.
    I have installed every brand of furnace sold in the US. Not one requires hard wiring and a fused disconnect per the manufacturer. If your furnace is installed that way it is because of local codes.
    Very few manufacturers list a minimum fuse. Most only list a maximum fuse or breaker size.
    Hobart Handler 175
    Hobart Iron Man 230 with spool gun
    Thermal Dynamics Cutmaster 52
    Makita Cold Cut Saw

    Possible future addition:
    Lincoln Invertec V311
    or Miller Dynasty 350
    or ???

  3. #23
    Join Date
    Mar 2011
    Location
    Apache Junction, Az
    Posts
    90

    Default

    Quote Originally Posted by kenwhite View Post
    The thing you have to consider when looking at the duty cycle, is that while the continuous current limit may be exceeded for short periods of time, the average current based on the duty cycle load is typically much less than rated continuous current.

    If the branch has multiple loads, the breaker would still trip trip if severly overloaded when multiple loads are being used - normally a thermal breaker is specified for this type of circuit.

    Article 630 is really written for commercial/light industrial use with exceptions for residential/home use of a welder.
    If a branch has multiple loads, the breaker size should equal the sum of the loads with the appropriate wire used. If the breaker is tripping as in your statement, then the wrong supply wire and breaker was installed. We install multiple appliances on a single circuit regularly for commercial buildings. We use a larger supply wire on that circuit and the larger breaker equal to the sums of the maximum of the appliances and each appliance has it's own individual fused disconnect with the appropriate size fuses for that one appliance.
    Hobart Handler 175
    Hobart Iron Man 230 with spool gun
    Thermal Dynamics Cutmaster 52
    Makita Cold Cut Saw

    Possible future addition:
    Lincoln Invertec V311
    or Miller Dynasty 350
    or ???

  4. #24

    Default

    There are 3 things that matter in any electrical installation, Breaker, (wire dia. size& length) and plug, The rule that must followed is: the breaker must always be the weak link. To get it right,,, you need to know your breaker size, the wire size and length of run and a proper plug or outlet for the amps.

    use this calculator to checkout your setup.......... if you are near the limit of one wire size run, use a larger dia. wire for safety in your design.

    http://www.gorhamschaffler.com/wire_...alculator.html

  5. #25

    Default

    Quote Originally Posted by A/C Guy View Post
    I have installed every brand of furnace sold in the US. Not one requires hard wiring and a fused disconnect per the manufacturer. If your furnace is installed that way it is because of local codes.
    Very few manufacturers list a minimum fuse. Most only list a maximum fuse or breaker size.
    That is funny because every HVAC forced hot air system I have seen is hardwired, and I did a quick search and found a few product manuals that require it too. In these manuals the manufacturer typically lists what type of safety disconnect and fuse/breaker is suggested too.

    I have never seen a maximum fuse size listed for a plug in device, only a mimimum size for proper operation to avoid excessive tripping.

    For hard wired devices, the recommended cable size, breaker/fuse, and disconnect is listed with the caveat that each installation is different and subject to local codes.
    Last edited by kenwhite; 03-27-2011 at 03:01 PM.
    __________________________
    Everlast Power I-MIG 200
    Everlast PowerUltra 205P
    Everlast SM 200-N
    Thermal Dynamics Cutmaster 42

  6. #26

    Default

    Quote Originally Posted by A/C Guy View Post
    If a branch has multiple loads, the breaker size should equal the sum of the loads with the appropriate wire used. If the breaker is tripping as in your statement, then the wrong supply wire and breaker was installed. We install multiple appliances on a single circuit regularly for commercial buildings. We use a larger supply wire on that circuit and the larger breaker equal to the sums of the maximum of the appliances and each appliance has it's own individual fused disconnect with the appropriate size fuses for that one appliance.

    Well, there are mimimum requirements for branch circuit design as well as load duty cycle, demand factor, requirements.

    I never said the breaker would trip excessively, I said it would still protect the branch correctly even when overloaded with many circuits on the branch energized at once.

    The rest of your post reinforces my previous points...

    Last edited by kenwhite; 03-27-2011 at 02:57 PM.
    __________________________
    Everlast Power I-MIG 200
    Everlast PowerUltra 205P
    Everlast SM 200-N
    Thermal Dynamics Cutmaster 42

  7. #27

    Default

    Quote Originally Posted by DiabolicZ View Post
    I could see that happening. Just for my general pacific 50 amp breaker and 8' of #6 wire, it cost me $80.
    lucky you only had to get 8'...I had to get 75'...I sure hope it was not in waste...Starting to like I would have been ok with 8awg for a welder that draws 42 amps
    sold my miller mig
    got a PT250EX
    saving up for a plasma cutter

  8. #28

    Default

    Quote Originally Posted by geezer View Post
    There are 3 things that matter in any electrical installation, Breaker, (wire dia. size& length) and plug, The rule that must followed is: the breaker must always be the weak link. To get it right,,, you need to know your breaker size, the wire size and length of run and a proper plug or outlet for the amps.

    use this calculator to checkout your setup.......... if you are near the limit of one wire size run, use a larger dia. wire for safety in your design.

    http://www.gorhamschaffler.com/wire_...alculator.html


    Geezer you must derate the ampacity of a cable if the wires are bundled togethter.

    Also, insulation type determines how much current a particular sized cable can carry. For example, 3 wires bundled together operating at 30*C (86*F) have the following ratings:

    6 AWG THHN -> 75A rating when at 30*C and can be operated all the way up to 90*C (194*F) with proper derating.

    6 AWG THHW -> 65A rating when at 30*C and can be operated all the way up to 75*C (167*F) with proper derating.

    6 AWG UF -> 55A rating when at 30*C and can be operated all the way up to 60*C (140*F) with proper derating.

    If there are more wires in the bundle than 3, the ampacity goes down. If the ambient around the wires is higher than 30*C, the ampacity goes down.

    So there is really more to correct power distribution design than just wire size and length...
    __________________________
    Everlast Power I-MIG 200
    Everlast PowerUltra 205P
    Everlast SM 200-N
    Thermal Dynamics Cutmaster 42

  9. #29

    Default

    There seems to be some confusion on demand factor and duty cycle, so I though I would try to clarify both.

    Demand factor is based on the premise that the actual load at any given instance in time will always be less than the sum of the total loads used within any given installation.

    If we add up all of the loads and size our electrical design for them -> microwave, TV, Stereo, garbage disposal, stove, furnace/air conditioning, etc, etc..., we would have very large, expensive, cable runs to handle a current draw that would not exist.

    So, the NEC allows for the total load to be reduced by a number called a "demand factor" when sizing branches - the breaker will still protect the wiring should the load for a given cable be exceeded under an unsual circumstance.

    ______________________________
    Now for the duty cycle explanation.

    Power is the rate of energy consumption per unit time -> Joules/Second.

    Joules are a form of heat, and internal heating is what damages the cable's insulation.

    In order to determine internal heating for a cable, I^2*R, the current must be measured in what is called Root/Mean/Square values - this value produces the same heating as an equivalent DC source.

    EXAMPLE: A current pulse of 100A that is turned on for 2 seconds and turned off for 8 seconds produces an RMS (heating value) calculated by:

    (100A)^2*2 seconds + (0A)^2*8 seconds -> Squared area = 20,000 A^2*S

    (20,000 A^2*S)/10 S -> Mean = 2000 A^2

    (2,000 A^2)^0.5 -> Root = 44.72 Amps

    So, you can see the 100 amp pulse described above only produces heating that is equivalent to a 44.72 Amp continuous current source, so why design for a 100 Amp circuit?


    The bottom line is that wiring is not a simple plug and play game, it requires some thought and experience.

    If you can't read and use the NEC effectively, then you should probably hire a qualified electrician to either help or perform the installation.
    Last edited by kenwhite; 03-27-2011 at 03:11 PM.
    __________________________
    Everlast Power I-MIG 200
    Everlast PowerUltra 205P
    Everlast SM 200-N
    Thermal Dynamics Cutmaster 42

  10. #30

    Default

    Quote Originally Posted by kenwhite View Post
    Geezer you must derate the ampacity of a cable if the wires are bundled togethter.

    Also, insulation type determines how much current a particular sized cable can carry. For example, 3 wires bundled together operating at 30*C (86*F) have the following ratings:

    6 AWG THHN -> 75A rating when at 30*C and can be operated all the way up to 90*C (194*F) with proper derating.

    6 AWG THHW -> 65A rating when at 30*C and can be operated all the way up to 75*C (167*F) with proper derating.

    6 AWG UF -> 55A rating when at 30*C and can be operated all the way up to 60*C (140*F) with proper derating.

    If there are more wires in the bundle than 3, the ampacity goes down. If the ambient around the wires is higher than 30*C, the ampacity goes down.

    So there is really more to correct power distribution design than just wire size and length...
    Interestings facts to be sure if the welder is being installed in a submarine or some other critical area with all the cables bundled, However my purpose is to simplify it for a fellow trying to make a single run from his panel box to the end of his shop/garage. Throwing in fractional calculations although accurate do not do any thing except add to his confussion. Rather than argue amongst ourselves about who is exactly right, let us step back and solve the problem for him in a form he may understand.

    The simplist answer I can give anybody is: when in doubt use a big thick wire

  11. #31

    Default

    Quote Originally Posted by geezer View Post
    Interestings facts to be sure if the welder is being installed in a submarine or some other critical area with all the cables bundled, However my purpose is to simplify it for a fellow trying to make a single run from his panel box to the end of his shop/garage. Throwing in fractional calculations although accurate do not do any thing except add to his confussion. Rather than argue amongst ourselves about who is exactly right, let us step back and solve the problem for him in a form he may understand.

    The simplist answer I can give anybody is: when in doubt use a big thick wire
    Well, the ampacity for a single cable installation is derated too, but that rarely occurs since everything needs at least a hot and return and a safety ground.

    While your advice may be sound in some instances, there is a lot more to electrical work than that.

    The OP discussion is about why it is "not recommended to over size a breaker" and there were many reasons/theorys discussed when it is appropriate to over size and when it is not.

    So while the technical discussion may be boring, it is required if you want to upgrade according to code which is based on safe, sound, operating principles that can be implemented in a some what easy and cost effective way.

    Last edited by kenwhite; 03-27-2011 at 09:11 PM.
    __________________________
    Everlast Power I-MIG 200
    Everlast PowerUltra 205P
    Everlast SM 200-N
    Thermal Dynamics Cutmaster 42

  12. #32

    Default

    The solution to this debate is actually a simple one..
    Apply for the proper 'permit', which is usually a requirement when adding to or upgrading an existing electrical panel/service, & the inspector will let you know whats 'required/acceptable' in your locale.
    -at the job-
    Miller Dynasty 200DX
    Miller Syncrowave 350
    MillerMatic 250 (several)
    Millermatic 350
    Miller Bobcat 250 (Service Truck)
    Lincoln AC225 (many)
    Miller Spectrum 625 Plasma (several)
    -At Home-
    Everlast PP256
    Longevity 256PI
    "Slow is smooth, smooth is fast.."

  13. #33

    Default

    Quote Originally Posted by ASE_MasterTech View Post
    The solution to this debate is actually a simple one..
    Apply for the proper 'permit', which is usually a requirement when adding to or upgrading an existing electrical panel/service, & the inspector will let you know whats 'required/acceptable' in your locale.
    You realize you just took all of the fun out of this thread, LOL

  14. #34

    Default

    Quote Originally Posted by ASE_MasterTech View Post
    The solution to this debate is actually a simple one..
    Apply for the proper 'permit', which is usually a requirement when adding to or upgrading an existing electrical panel/service, & the inspector will let you know whats 'required/acceptable' in your locale.
    Or Call a licensed and insured electrical contractor and sleep well at night.
    Last edited by Ram48; 03-27-2011 at 10:57 PM. Reason: Sp error
    Everlast I mig 205
    Everlast 200 amp spool gun
    Everlast 250 ex
    H. F. 12x36 lathe
    Grizzly Mill
    10,000 lb two post lift
    Box and Pan Brake
    Bead roller
    jet 5x7 horizontal band saw
    Wilton 14 inch vertical band saw
    Mitec 50 A plasma cutter.
    tool grinder
    20 ton press and press brake
    more power and hand tools then I can list here
    Dodge Neon that runs 10.23 @143 mph in the quater
    70 Chevelle convert
    It took 62 years But I finally have my dream Garage

  15. #35

    Default

    Quote Originally Posted by Ram48 View Post
    Or Call a licensed and insured electrical contractor and sleep well at night.
    Yep, and I think I said that once or twice...

    __________________________
    Everlast Power I-MIG 200
    Everlast PowerUltra 205P
    Everlast SM 200-N
    Thermal Dynamics Cutmaster 42

  16. #36
    Join Date
    Apr 2011
    Location
    Sasktachewan, Canada
    Posts
    95

    Default

    I can think of only one anwser to this post:

    "There is never time to do it right but there is always time to do it over!"
    Attitude Determines Altitude

  17. #37

    Default

    Quote Originally Posted by Canada View Post
    I can think of only one anwser to this post:

    "There is never time to do it right but there is always time to do it over!"
    There's not always time to 'do it over', particularly when your house/shop is a pile of ash.
    just a thought...
    -at the job-
    Miller Dynasty 200DX
    Miller Syncrowave 350
    MillerMatic 250 (several)
    Millermatic 350
    Miller Bobcat 250 (Service Truck)
    Lincoln AC225 (many)
    Miller Spectrum 625 Plasma (several)
    -At Home-
    Everlast PP256
    Longevity 256PI
    "Slow is smooth, smooth is fast.."

  18. #38
    Join Date
    Apr 2011
    Location
    Sasktachewan, Canada
    Posts
    95

    Default

    There's not always time to 'do it over', particularly when your house/shop is a pile of ash.
    just a thought...
    That was the point. How many times have you heard someone say they don't have time to do it right. After it fails they always find time to do it over. In other words do it right the first time, every time.
    Attitude Determines Altitude

Similar Threads

  1. Breaker size for 255EXT?
    By Seshan in forum General Welder Questions
    Replies: 16
    Last Post: 07-20-2014, 02:10 PM
  2. Looking for Special 12 VDC Circuit Breaker
    By cbmkr in forum Tips & Tricks, Custom Tools, Safety, Ideas and Reviews.
    Replies: 11
    Last Post: 12-03-2012, 01:43 PM
  3. Sizing the neutral
    By posixPilot in forum General Welder Questions
    Replies: 12
    Last Post: 01-28-2012, 04:52 PM
  4. 30 amp breaker for PM205
    By www in forum Multi-Process Units (TIG,Stick,Plasma/MIG,TIG,Stick Combo units)
    Replies: 12
    Last Post: 04-27-2010, 05:57 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •