You guys know what size breaker and wiring size I should install for the powermaster 226? Wiring will be no longer than 35'.
Thanks in advance
You guys know what size breaker and wiring size I should install for the powermaster 226? Wiring will be no longer than 35'.
Thanks in advance
I saw your post over on Pirate and wanted to post but didn't have an account yet.
Okay...keep in mind a local check with building codes is always advised, and depending upon your location, a building permit may be required. If I want to pour a concrete walk to my front door, or want to change the carpet, where I live a building permit is "required".
If I remember right the Amperage is about 36 amps...At least for the
PowerTig, both of which have same maximum ratings on output.
I believe you'll need a 40 amp breaker and a minimum 8 gauge wire....But I'd say a 6 gauge wire would be better...That is if you are using copper. Aluminum wiring requires a much larger wire.
Mark
performance@everlastwelders.com
www.everlastgenerators.com
www.everlastwelders.com
877-755-9353 x204
M-F 9am - 5pm EST
Thanks mark, I figured it was a 40amp breaker. Thanks for the advice bud. There not as strict in my area about codes, but I actually had the shop built and didnt even bother with those greedy bastards on the entire shop this time LOL
Wait till the tax assessors roll around...and they don't show a record of that shop....
Put the wheels under or around it and call it a Mobile Shop and they can't get that money...lol
Mark
performance@everlastwelders.com
www.everlastgenerators.com
www.everlastwelders.com
877-755-9353 x204
M-F 9am - 5pm EST
Here, a lesson learned after, is a shop that is the mass produced(what I consider lighter weight) material is treated the same as those "metal garage" type deals and are not required to have all the extra crap that comes with a new structure.
Reguardless, I dont mind paying the taxes on it they were just trying to put me through HELL
You must also consider the length of the wire and the operating or environmental temperature when selecting the size of the wire. If you do use the aluminum wire be sure to use a compatible receptacle and apply the corrosion inhibitor at the connection. Number 8 copper is good for 40-55 amps depending on the type selected based on the insulation and application but the same gauge in AL is only good for 30-45 amps. Number 6 copper will safely carry 55-75 amps in a heat range up to 140-190 deg. F. If you are not sure it’s best to step up the wire size and unless you really are sure how to properly install aluminum wire it’s safer to stay with the copper. You pay more for it but it is safer than a corroded connection starting a fire. For reference you can get a copy of the National Electrical Code book at your local library. Another thing is to make sure the ground lead matches or exceeds the size of the feeds.