Can you run a PW140 on 208 vac
Can you run a PW140 on 208 vac
you must have 3 phase
EVERLAST 250 EX , EVERLAST I-MIG 205 , EVERLAST spool gun NOW have 2 EVERLAST POWER PLASMA 50 plasma cutter's , LINCOLN 175HD MIG WELDER , VICTOR TORCH SET and many more tools to many to list
????? how does that remotely answer my question. I am asking if I take 2 120vac legs from a 120/208 3 ph panel and a Neu/GRND legs would it hurt the Powerarc 140. It is not much different than 2 120vac legs from 120/240 1ph
because only 208 i know of is 3 phase but there 3 phase is different from the usa . because 2 legs single phase of is 120 120 total 240 read this article that's why i asked 3 phase http://en.wikipedia.org/wiki/Three-phase_electric_power .. dude just trying to help sorry if i offended you
EVERLAST 250 EX , EVERLAST I-MIG 205 , EVERLAST spool gun NOW have 2 EVERLAST POWER PLASMA 50 plasma cutter's , LINCOLN 175HD MIG WELDER , VICTOR TORCH SET and many more tools to many to list
How many 110v lines are in a 3 phase? 3? or is it 3 - 220v breakers?
Purple Fabricator 211i
3 phase comes 2 ways there is 4 wires coming in to box it makes 240 volt if only 3 wires coming in to box will make 208 . my shop has 4 wire coming in to my 3 phase box at my shop
EVERLAST 250 EX , EVERLAST I-MIG 205 , EVERLAST spool gun NOW have 2 EVERLAST POWER PLASMA 50 plasma cutter's , LINCOLN 175HD MIG WELDER , VICTOR TORCH SET and many more tools to many to list
Three phase power comes in two flavors.
Star and Delta.
Star has 4 leads - 1 for each of three windings, and 1 neutral which is the common connection point for each winding.
So for low voltages, this arrangement gives 208 volts between any pair of hot leads, and 120 volts from any hot lead to neutral.
Delta has 3 leads.
This arrangement gives 240 volts between any pair of leads. There is no 120 volts, unless a winding has a center tap.
I've omitted the ground wire in both cases.