Thread: Input power wire question 250EX

  1. Default Input power wire question 250EX

    What would the recommended type and ga. wire for a 60ft run be?

    Machine is a 250EX.
    220v 3 wire hookup.

  2. #2

    Default

    No 8 should do the trick, with a 50 amp breaker, you can verify this by using one of the many wire size calculators available on the web.

  3. Default

    Thank you. I picked up the #8 wire, 50Abreaker, plug, receptacle and Argon bottle today. I should have it wired this weekend and the water cooler should be here Monday.

  4. #4
    Join Date
    Oct 2011
    Location
    Litchfield Park, AZ
    Posts
    370

    Default

    Quote Originally Posted by AWDnot2 View Post
    Thank you. I picked up the #8 wire, 50Abreaker, plug, receptacle and Argon bottle today. I should have it wired this weekend and the water cooler should be here Monday.

    I have ran the stock 2.5 mm^2 cord supplied with the 250 EXT and had no problem stick welding at 200 amps. For power from the main barker, I have the machine tied to a 40 amp breaker with No. 8 wire. The No. 8 wire should be fine as long as it is not too long.
    Miller 252
    PowerTig 250 EXT
    Evolution Rage 2
    48X6 inch Belt Sander w/ 9 inch Disk Sander
    ...

  5. #5

    Default

    Quote Originally Posted by DVA View Post
    I have ran the stock 2.5 mm^2 cord supplied with the 250 EXT and had no problem stick welding at 200 amps. For power from the main barker, I have the machine tied to a 40 amp breaker with No. 8 wire. The No. 8 wire should be fine as long as it is not too long.
    A 40 amp breaker would not work at my shop on the 250EX as I was getting 208 volts off the 3phase supply and the inrush would pop the breaker, so I had to run over reset the breaker and run back and turn on the 250Ex again so it would run before the capacitators bleed down,,,,worked fine once I got it started,,,,took me a while to figure out that 208 volts requires a larger breaker on the supply side for the in rush demand of the machine...if I had 220 or 240 volts a 40 amp breaker would be fine...
    Some of those lies people tell about me, are true

Similar Threads

  1. Power iMIG 275P Wire Feeder Alignment Question
    By Baronsbest in forum MIG Welding (GMAW/GMAW-P/FCAW)
    Replies: 2
    Last Post: 05-22-2016, 06:01 PM
  2. Power Tig 250EX question
    By 11Bravo in forum TIG Welding (GTAW/GTAW-P)
    Replies: 5
    Last Post: 11-17-2014, 03:28 PM
  3. PowerArc 140st input amps question
    By MotoJ in forum Stick Welding (SMAW)
    Replies: 8
    Last Post: 10-02-2012, 05:34 PM
  4. Input Power Requirments for the 250EX
    By sschefer in forum TIG Welding (GTAW/GTAW-P)
    Replies: 25
    Last Post: 11-02-2010, 04:44 AM
  5. PowerTig 250EX input amps
    By JJW in forum TIG Welding (GTAW/GTAW-P)
    Replies: 2
    Last Post: 08-04-2009, 04:32 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •