  1. Default What gauge to wire a 50 amp line?

    I have a 20 amp 220 for my small welders but decided I might as well run a 50 amp along side. It's just a 25' run from the service box. I have plenty of 12/2 romex around but wasn't sure what would be appropriate for a 50 amp line.

    TIA


    P.S.
    I now have a 225LX and waiting for a PP50
    Charlie

    Everlast 225 LX
    Everlast PP 50

    HF 130 TIG/90 ARC
    HF 90 fluxcore

    ATX MIG (don't ask)

  2. #2
    Join Date
    Jan 2010
    Location
    Chugiak , Alaska
    Posts
    259

    Default Input Cable Sizing

    Technically 12 Ga. will handle 50 amps, but I would go with at least 10Ga.
    Here’s a link to calculate minimum conductor sizing.
    http://www.elec-toolbox.com/calculators/voltdrop.htm
    ____
    Ray

    Everlast Sales and Support Team.
    support@everlastalaska.com
    www.everlastalaska.com

    877-755-9353 X207

  3. #3

    Default

    Quote Originally Posted by jtybt View Post
    I have a 20 amp 220 for my small welders but decided I might as well run a 50 amp along side. It's just a 25' run from the service box. I have plenty of 12/2 romex around but wasn't sure what would be appropriate for a 50 amp line.

    TIA


    P.S.
    I now have a 225LX and waiting for a PP50
    At Home Depot today I bought 4-conductor 10 gauge, recommended by the salesperson. It was about $2.00 per foot.

  4. Default

    $2.00 a ft! OUCH.

    To complicate matters, I have a 10 Ga 25' extension cord putting total run at 50' so I presume 10 Ga Romex is much better.

    What is the fourth wire for? Ground? I have a Leviton 50 amp dryer plug with no ground.
    Charlie

    Everlast 225 LX
    Everlast PP 50

    HF 130 TIG/90 ARC
    HF 90 fluxcore

    ATX MIG (don't ask)

  5. #5

    Default

    You should run 6 ga. wire for a 50 amp circuit.

    sg

  6. #6

    Default

    I agree, especially any distance from the panel box.

  7. Default

    What would be the amp draw of the 225LX or the PP50...not being used at the same time.

    The calculator link said 10 ga up to 50'. I measured the actual run, 24'.

    Electrician at HD said the line and breaker should be matched to the unit being used.

    Actually sounds to me that it's OK to used larger gauge wire as well as plugs and receptacles as long as the breaker matches the 'appliance' being used?????
    Charlie

    Everlast 225 LX
    Everlast PP 50

    HF 130 TIG/90 ARC
    HF 90 fluxcore

    ATX MIG (don't ask)

  8. #8

    Default

    Quote Originally Posted by jtybt View Post
    $2.00 a ft! OUCH.

    To complicate matters, I have a 10 Ga 25' extension cord putting total run at 50' so I presume 10 Ga Romex is much better.

    What is the fourth wire for? Ground? I have a Leviton 50 amp dryer plug with no ground.
    One wire is ground (green), one is white (neutral), one is red (hot) and the other is black (hot). Good luck!

  9. #9

    Default

    You could wire color for color and trim the red wire or other color wire, whatever color it may be. Just be sure to hook up the green ground wire to the middle round post. The 4th wire is considered a safety ground. If you will observe in some true NEMA welder type plug connections, there are actual wire colors printed on the plug itself, showing you what color to use. They all say black and white for the two hot legs and green for ground. I would not use the red if this is an extension type plug, just use the colors that are used in the welder if it terminates into a male plug and not directly into the panel box.

  10. Default

    Turns out I already had 10/2 with a 20 amp breaker. Upgraded to 40 amp breaker and 50 amp plugs/receptacles.
    Charlie

    Everlast 225 LX
    Everlast PP 50

    HF 130 TIG/90 ARC
    HF 90 fluxcore

    ATX MIG (don't ask)

  11. Default

    i really hope your not saying your gonna try and run 40 amps through 10 ga wire. if so i hope you have a good house insurance policy. for a 40 amp breaker you should be running atleast #8 and for a 50 you should be running a #6 otherwise you will be getting that wire red hot when pulling a max load and too many hot cold cycles will make the insulation melt off and crack and eventually creating a short in the walls or whereever the wires run which will in turn eventually burn your house down.

    i've been an electrician for 17 years now and have seen people do this waay too many times for my own comfort and wonder why heir house burnt down or why their equipment burns up. the problem with running a smaller gauge wire for a larger circuit is it won't flow as well as the larger wire which in turn causes more resistance. the resistance in the wire makes the welder work harder to accomplish the same thing because it's not getting what it needs to do the job.

    picture a 2" water line being used to fill a swimming pool now put a section of 1/2" at the end of that 2" line. your basically doing that same thing by using a wire that's too small for the load. your connection at the breaker are gonna heat up, the wire itself is gonna heat up, and your welder is gonna heat up because of all the effort it's putting into trying to get what it needs. somewhere something is gonna fail. most of the time it's the it's the appliance trying to be used but the other times it's either the wire or the breaker and either 1 of those are very adept at starting a fire

  12. Default

    oh and by the way read the sentence at the top of the page of that link. he tells you his calculations aren't up to code and to reference the nec to make sure he's right

  13. #13

    Default

    Checked the price today for the 6AWG/2. Lowes had the cheapest price. HD was over $3/ft. I will be running the #6 to my 50A outlet. Copper prices are getting up. Who would thought that copper would follow gold and silver as a precious metal.
    Lincoln Weld-Pak 100 (C-25 or CO2 Shield)
    Victor Oxy-Act
    Lincoln AC225 Tombstone
    Everlast 250EX & W300 Cooler

  14. #14
    Join Date
    Mar 2011
    Location
    The Boonies of Texas
    Posts
    420

    Default

    China is thinking about backing their currency with copper. If that happens watch out, old pennies (the solid copper ones) will be like dimes or better. I had a shop fire 10 years ago and finally am getting around to cleanup of the copper (welders, wiring, cable etc.) I took it to the metals recyclers Tuesday and got $344 for 106 lbs of badly burned copper. I just finished putting in a new 50A circuit for my Lincoln Tombstone AC welder yesterday. Luckily I had just enough #6 left over from a few years back at 50 cents a foot.

    Thurmond
    Last edited by Tritium; 04-16-2011 at 01:38 AM.
    Miller Bobcat 3 Phase,
    Miller Suitcase X-Treme 12VS wire feeder for the Bobcat with M-25 300A .045" gun / Bernard 400A 5/64" wire mig gun .
    26 series gas cooled TIG torch, setup for quick connect to Bobcat.
    17 series gas cooled Tig Torch for Low Amp Solar Tig (Direct Solar Panel Powered Tig welding)
    Hobart Handler 187 Mig / Fluxcore
    EVERLAST PowerUltra 205P
    EVERLAST PowerTig 250 EXT 2013 Model

Similar Threads

  1. 14 gauge sheetmetal tig ballpark ??
    By braveops in forum Multi-Process Units (TIG,Stick,Plasma/MIG,TIG,Stick Combo units)
    Replies: 5
    Last Post: 11-13-2013, 05:36 AM
  2. Replies: 26
    Last Post: 02-22-2012, 12:25 PM
  3. Gauge of HF ground wire?
    By Zman0690 in forum General Welder Questions
    Replies: 8
    Last Post: 08-24-2011, 12:25 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •