    I've been meaning to ask this for a while now. First let me explain my setup. On the far wall of my garage I have my 240V outlet which s about 1ft away from the breaker panel. My work area is on the other end of my 3 car garage so to get power to the welder I use a 6ga 30ft RV extension cable. The outlet is a 4 prong outlet with Phase 1, Phase 2, Neutral, and ground. The RV extension cable is the same. The welder has a four prong plug on it now but the earth ground lead is not plugged in.

    Now the issue. If everything is plugged in and I flip the switch on the back of the welder the breaker in the panel trips. If I first turn on the switch and plug the welder into the RV extension cable the breaker in the panel trips. If I first turn on the welder and plug the RV extension cable into the outlet there is a little bit of flash arcing but everything is fine.

    Anyone run into this before? Ideas?
    My Stuff:
    Everlast PP256
    Century Mig 135
    BladeRunner Inverted Jig Saw
    HF 14" Chop Saw
    Box full of HF 4" Angle Grinders
    Home made tank roller!

  2. Default

    What size breaker is it?

    And you're saying it trips just from powering-on? No welding yet?

    Do you use this breaker for anything else that has a significant load without problems? Could that breaker just be old & tired?

  3. #3
    Join Date
    May 2012
    Location
    Disneyland
    Posts
    2,662

    Default

    Sounds like the breaker is not able to handle the inrush current. As mentioned, either old or not large enough. Also you should be using the ground for your welder, not the neutral. The machine only requires the two phase lines and the ground. The max inrush for a PP256 is listed as 42 amps. So even a 40A might nuisance trip, if it was old or has been cycled a bunch.
    Long arc, short arc, heliarc and in-the-dark!

  4. #4

    Default

    Quote Originally Posted by Rambozo View Post
    Sounds like the breaker is not able to handle the inrush current. As mentioned, either old or not large enough. Also you should be using the ground for your welder, not the neutral. The machine only requires the two phase lines and the ground. The max inrush for a PP256 is listed as 42 amps. So even a 40A might nuisance trip, if it was old or has been cycled a bunch.
    Brand new 50A breaker.
    My Stuff:
    Everlast PP256
    Century Mig 135
    BladeRunner Inverted Jig Saw
    HF 14" Chop Saw
    Box full of HF 4" Angle Grinders
    Home made tank roller!

  5. #5

    Default

    Quote Originally Posted by Blaster View Post
    What size breaker is it?

    And you're saying it trips just from powering-on? No welding yet?

    Do you use this breaker for anything else that has a significant load without problems? Could that breaker just be old & tired?
    Breaker is there just for the welder, like I said above brand new 50A
    My Stuff:
    Everlast PP256
    Century Mig 135
    BladeRunner Inverted Jig Saw
    HF 14" Chop Saw
    Box full of HF 4" Angle Grinders
    Home made tank roller!

  6. #6
    Join Date
    Oct 2010
    Location
    Northern Virginia
    Posts
    1,323

    Default

    Just to remove one variable from the equation: can you plug the welder directly into the outlet, without using the RV extension cable? Just wondering if there might be some fault in the extension.
    DaveO
    Oxweld oxy acet gear
    IMIG 200
    PowerTIG 210 EXT... Amazing!

  7. #7
    Join Date
    May 2012
    Location
    Disneyland
    Posts
    2,662

    Default

    Quote Originally Posted by Ron66 View Post
    Brand new 50A breaker.
    Is it a GFCI type? Have you wired the welder plug to use the ground pin? Something is not right here. Tripping a 50A breaker is nothing to ignore or work around. It takes a lot more than 50A to trip one instantly. Also brand new doesn't guaranty you got a good one.
    Last edited by Rambozo; 07-31-2014 at 11:04 PM.
    Long arc, short arc, heliarc and in-the-dark!

  8. #8

    Default

    If it's a GCFI, it may not work well. Also, if you have tried to match wire colors, then it is trying to run on 120V.

  9. #9

    Default

    Grab a meter, set to 700VAC, check from the ground to each leg/phase and make sure you have 120VAC at the plug (wall and RV cord). Then check across the two legs for 240VAC. This lets you know it is not wiring.

    Should just need ground and 2 120VAC out of phase legs to run it on 220VAC.

    And pictures of the plugs and outlets?
    Mike R.
    Email: admineverlast@everlastwelders.com
    www.everlastgenerators.com
    www.everlastwelders.com
    877-755-9353 x203
    M-F 12 - 7PM PST
    FYI: PP50, PP80, IMIG-200, IMIG-250P, 210EXT and 255EXT.

  10. #10

    Default

    Quote Originally Posted by everlastsupport View Post
    Grab a meter, set to 200VAC, check from the ground to each leg/phase and make sure you have 120VAC at the plug (wall and RV cord). Then check across the two legs for 240VAC. This lets you know it is not wiring.

    Should just need ground and 2 120VAC out of phase legs to run it on 220VAC.

    And pictures of the plugs and outlets?
    I have the 2 phases and neutral wired with a separate earth ground rod outside the ground to dump the arc start noise. The welder works perfect and I routinely use it at 160 - 180A with no problems at all using the RV extension cable. Does the welder use any 120V off one of the phases? Or is it straight 240V? Also this only happens the first time I turn it on. I can turn it off and back on at the welder once the initial surge happens and the caps are charged without a problem. The only thing I'm wondering is if the RV cable is very inductive and I'm seeing some kind of large current spike due to reactance when the caps initially charge.
    My Stuff:
    Everlast PP256
    Century Mig 135
    BladeRunner Inverted Jig Saw
    HF 14" Chop Saw
    Box full of HF 4" Angle Grinders
    Home made tank roller!

  11. #11
    Join Date
    May 2012
    Location
    Disneyland
    Posts
    2,662

    Default

    The machine is straight 240 and should not have a neutral line at all. (I am aware that the neutral and ground are most likely bonded at the panel)
    The machine should never draw the kind of amperage that would pop a 50A breaker.
    You never did answer if it is a GFCI breaker. A GFCI can trip for reasons other than over-current while a regular breaker doesn't.
    A typical 50A breaker can take 100A for about 10 seconds before tripping, so if it is indeed instantly tripping from over-current, something is very wrong.
    No way a 30' cord could have that kind of inductance, even if it was wound into a tight coil.
    Long arc, short arc, heliarc and in-the-dark!

  12. #12

    Default

    Quote Originally Posted by Ron66 View Post
    I have the 2 phases and neutral wired with a separate earth ground rod outside the ground to dump the arc start noise. The welder works perfect and I routinely use it at 160 - 180A with no problems at all using the RV extension cable. Does the welder use any 120V off one of the phases? Or is it straight 240V? Also this only happens the first time I turn it on. I can turn it off and back on at the welder once the initial surge happens and the caps are charged without a problem. The only thing I'm wondering is if the RV cable is very inductive and I'm seeing some kind of large current spike due to reactance when the caps initially charge.
    Use the ground and two hot legs, not the neutral (see my last post and Rambozo's). See if that does it. Does it only do this with the RV cord and not the wall outlet (assuming the same plug type)? Is it GFCI like Ram asked?
    Mike R.
    Email: admineverlast@everlastwelders.com
    www.everlastgenerators.com
    www.everlastwelders.com
    877-755-9353 x203
    M-F 12 - 7PM PST
    FYI: PP50, PP80, IMIG-200, IMIG-250P, 210EXT and 255EXT.

  13. #13

    Default

    So there won't be any return current on the ground from one of the phases right? I'd hate to energize my earth ground. And no this is not a gfi breaker. I didn't know that you could get a double 50A as a gfi!
    My Stuff:
    Everlast PP256
    Century Mig 135
    BladeRunner Inverted Jig Saw
    HF 14" Chop Saw
    Box full of HF 4" Angle Grinders
    Home made tank roller!

  14. #14

    Default

    I think you need to call an electrician to sort out your electrical problem
    EverLast 140ST
    PowerPlasma 50
    No You Can't Use Them

  15. #15

    Default

    Quote Originally Posted by Gerry View Post
    I think you need to call an electrician to sort out your electrical problem
    I agree, if he does not know how to wire it, that would be the safest thing.
    Mike R.
    Email: admineverlast@everlastwelders.com
    www.everlastgenerators.com
    www.everlastwelders.com
    877-755-9353 x203
    M-F 12 - 7PM PST
    FYI: PP50, PP80, IMIG-200, IMIG-250P, 210EXT and 255EXT.

  16. #16

    Default Wiring

    Quote Originally Posted by Ron66 View Post
    I've been meaning to ask this for a while now. First let me explain my setup. On the far wall of my garage I have my 240V outlet which s about 1ft away from the breaker panel. My work area is on the other end of my 3 car garage so to get power to the welder I use a 6ga 30ft RV extension cable. The outlet is a 4 prong outlet with Phase 1, Phase 2, Neutral, and ground. The RV extension cable is the same. The welder has a four prong plug on it now but the earth ground lead is not plugged in.

    Now the issue. If everything is plugged in and I flip the switch on the back of the welder the breaker in the panel trips. If I first turn on the switch and plug the welder into the RV extension cable the breaker in the panel trips. If I first turn on the welder and plug the RV extension cable into the outlet there is a little bit of flash arcing but everything is fine.

    Anyone run into this before? Ideas?
    Your RV plug is for 120 volts only if you have a 4 wire RV plug it is still 120 volts, unless you have changed some things.Most 4 prong RV twist lock connectors are marine connectors which have an extra neutral or ground. These are used and added to RVS for various reasons including stopping red ants from following the cord into the camper.
    Please remember RV cords and plugs are for 120 volts operation, I have repaired many blown RV power systems because someone plugged there RV into a welder outlet.


    Your 50 amp plug on your welder has 3 prongs 2-120 prongs when combined give you 240 volts and one half round prong center top which is the ground.
    Yes there is voltage present in the ground or neutral wire when you machine or whatever is plugged in and operating. Electricity must have a ground to work.

    To make your breaker trip 2 things need to happen overheating from to much power draw or a short in the circuit in your wiring a sudden trip is a short slow is overheating , thus more than likely your wiring is crossed somewhere causing the trip..
    PowerTig 200DX
    Supercut 50P
    PowerTig Micro 185 SOLD GREAT MACHINE
    Millermatic 200
    Miller Thunderbolt
    Jet 1340 Lathe
    Jet 20" Drill Press
    Jet 12" Wet Band Saw
    Kalamazoo H7 Bandsaw
    Forward 12,000 lb 4 Post Lift

  17. #17

    Default

    Actually a lot of RV outlets are two 120 legs, but from the same power leg as most "220" RV cables don't measure power unless directly to ground. A lot of campsites and RV hookups do this because everything in a camper is 120V so it does not matter or need to be off separate power legs.

  18. #18

    Default

    Quote Originally Posted by performance View Post
    Actually a lot of RV outlets are two 120 legs, but from the same power leg as most "220" RV cables don't measure power unless directly to ground. A lot of campsites and RV hookups do this because everything in a camper is 120V so it does not matter or need to be off separate power legs.
    Correct thus not creating a true 240 volt power source, and not frying your power supply and other things.
    PowerTig 200DX
    Supercut 50P
    PowerTig Micro 185 SOLD GREAT MACHINE
    Millermatic 200
    Miller Thunderbolt
    Jet 1340 Lathe
    Jet 20" Drill Press
    Jet 12" Wet Band Saw
    Kalamazoo H7 Bandsaw
    Forward 12,000 lb 4 Post Lift

  19. #19

    Default

    See post 9 for testing. If they are out of phase he will see 240VAC.
    Mike R.
    Email: admineverlast@everlastwelders.com
    www.everlastgenerators.com
    www.everlastwelders.com
    877-755-9353 x203
    M-F 12 - 7PM PST
    FYI: PP50, PP80, IMIG-200, IMIG-250P, 210EXT and 255EXT.

Similar Threads

  1. Looking for Special 12 VDC Circuit Breaker
    By cbmkr in forum Tips & Tricks, Custom Tools, Safety, Ideas and Reviews.
    Replies: 11
    Last Post: 12-03-2012, 01:43 PM
  2. Circuit Breaker Dissection
    By jakeru in forum Personal Projects (no welder required)
    Replies: 6
    Last Post: 03-22-2012, 05:10 PM
  3. 30 amp breaker for PM205
    By www in forum Multi-Process Units (TIG,Stick,Plasma/MIG,TIG,Stick Combo units)
    Replies: 12
    Last Post: 04-27-2010, 05:57 PM
  4. breaker/wiring size?
    By singlesupra in forum General Welder Questions
    Replies: 5
    Last Post: 09-02-2009, 08:45 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •