Originally Posted by
ChuckD
Just to follow up I tested the voltage coming through the circuits. The 15 amp circuit travels about 40 ft from the service box to the plug by the time it travels to the back of my garage. The 30 amp circuit travels about 6 ft from the service box to the plug. When measured at the plug the difference between the two is about 9 volts. My contractor accounts this to voltage drop and it is common with how many of the homes are wired around here. We had the same problem with the outdoor outlets at the back of my home which is the furthest distance away from my service box. The service at that location was so weak that certain items would not work if plugged in, but common items like a radio would. According to code it's fine, but this might be what is causing my problem. Using the 30 amp circuit the iMig is performing above my expectations.
Chuck
To get an accurate reading, you need to measure the voltage when the circuit is under load. I would bet you will see a lot more than a 9 volt drop when welding. Also, a 9 volt drop over 40 feet is not good, either. I would suspect that there are some poor connections along that circuit. Even with a full 15 amp load the voltage drop over 40 feet should be only 3 volts. Running a heavy load like a welder will bring out problems in wiring that might go unnoticed with light loads.